Difference between DH+ and DH485 Port on AB SLC505 PLC's

Yes they are different


An SLC 503 uses DH485
A SLC 504 uses DH+
A SLC 505 uses Ethernet

All of them also have an RS 232 port as well

Understood and we are aware of that! Our current setup: CPU SLC504 has DH+ port. Talks to Panelview on that port. We need to upgrade to SLC 505 as we need to network (Don't want to use 1761-NET-ENI) on ethernet. Can the RS232 port of the SLC 505 be reconfigured to talk to the panelview on DH+. The manual indicates that the RS232 can be configured to DH485. Hence my question what the difference is between DH485 and DH+, and can the existing Panelview talk to the RS232 port?
 
No the serial port cannot be used for DH+.
What is the catalog number of the PanelView?
(first rule when asking anything about PanelViews is to supply the part number)

Alan
I am not on the plant at present. Was just pre-empting - type of what /if scenario. Will get all the details and then will revert back to if needs be. Thank you for the assist.
 
I am not on the plant at present. Was just pre-empting - type of what /if scenario. Will get all the details and then will revert back to if needs be. Thank you for the assist.

It may be easier to toss in an Ethernet to DH+ gateway. I tossed one in on a PLC5 system that goes to wireless. The ship's have a PV+ to access the land based system so it can operate the system remotely. IIRC, the unit was about 1900 bucks from Prosoft. Worked great. I could be anywhere within wireless range and have access to everything. Pretty sweet!

Another DH+ rig (dual 542's) and a 1500P (panel puter). The guy who set this up did not know that this had RSLinx Gateway. After a few minutes of configuration, I am sitting out in the parking lot, in my truck, online -via- wireless. No problems what so ever. Worked great.

My baby router is a Cradlepoint CTR35, and this thing has some range to it.
 

Similar Topics

Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
Replies
7
Views
1,411
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
Replies
28
Views
4,038
Good Morning , I have 2 Frequency Drive panels to build and commission . It is for 2 pump systems . Just wondering , what is the...
Replies
4
Views
1,971
Hi Experts, Good day! What are the differences between PCS7 SIMATIC Batch and PM Control? Do you have any manual like "Getting Started "...
Replies
0
Views
809
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
Replies
9
Views
2,822
Back
Top Bottom