hello... i'm trying to take an analog value from transmitter..
i'm using OMRON CS1G-CPU45, and the analog module is CS1W-AD16,
the analog value is 1-5V, i have measured the analog value on the Analog module and the vaule is 4.3V, but whe i checked on CX programmer the vaule is nothing...please help me..
here's the wiring graph, ladder configuration and the i/o table configuration(i use channel 6 and 7):

070920121389a.jpg
 

Attachments

  • 1.bmp
    159.5 KB · Views: 21
  • hh.bmp
    163.2 KB · Views: 10
Did you add the analog module without shutting down the PLC? Many PLCs do not like a module to be inserted with the power on. Check your manual to see the correct procedure for adding a module to the PLC I/O configuration.
 

Similar Topics

I have a Mitsubishi FX2N-64MR-UA1 processor. The 1st analog output card is an FX2N-4DA. It requires 24VDC power. That card is obsolete. The card...
Replies
1
Views
1,559
Hi I'm working on a project for a client who needs to automate the feed from a conveyor into a densifier powered by a 250hp 480v motor. I've...
Replies
14
Views
2,671
Hi, I am pretty good with Rockwell gear but I am fairly green when it comes to Siemens and I am having difficulty finding where an analog ASi...
Replies
11
Views
3,966
I can’t able to get data from IN16I analog card, signal type 4-20 ma System configuration Rack 1 Slot-0, L551 CPU Slot-1, BSN Rack 2...
Replies
1
Views
2,067
I'm having trouble configuring my 1734-OE4C 4ch analog out modules. I've read the docs but details on configuration is sketchy at best, at least...
Replies
3
Views
3,594
Back
Top Bottom