I have a 1771-HSN/B card in a piece of equipment. I have a "system" led that is red on the card. That's usually a bad thing. We have an E-Stop associated with the card. I have a PLC program without descriptions but I've worked out the E-Stop is tied to the card. I was hoping to find out if it is a recoverable fault. I have tried Rockwell's knowledge base for information on the card and can't find anything. Would anyone know where else I might look?
 
That's bad news.

The 1771-HSN is a single-axis motion controller, also called an "IMC-120". The "N" designated that the module was shipped without a memory module; you'll probably find one inside.

The software to configure it is called "ODS". You can still get the User Manual for ODS software from the RA Literature Library:

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/8520om-um051_-en-p.pdf

Use the keyword "IMC" in the literature library search and you'll find the IMC-120 installation guide and user guide.

I think the IMC-120 might be to the point where RA doesn't offer anything but repair services.
 
Thanks Ken. The manual should be a big help. Did you know to use the "IMC" in the search or did I overlook something?
 

Similar Topics

Good morining all. What a great Monday! We all made it through the tornadic weather Friday except this one machine that was here to greet me this...
Replies
0
Views
1,907
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
Replies
3
Views
365
Existing environment shown in attached photo (Existing.jpeg) Proposed Environment shown in attached photo (New.jpeg) I am migrating a PLC5 system...
Replies
0
Views
590
I have a 1756-L81e v32 using a DHRIO v7.001 in RIO scanner Driving (7) 1771 ASB Modules @ 115k baud. The Racks RPI are set at 48msecs. This system...
Replies
2
Views
896
Hello, I am setting up for practice and I am having trouble seeing the 1771 Scanner in RsLinx as well as Rsnetworx My setup: slot 0 : PLC-5/40E...
Replies
3
Views
976
Back
Top Bottom