Anyone got an easy way to find the IP address, bought off of ebay and it appears the config screen is passworded. Since it has a write error to 193.168.200.1 I figured the address had to be close to the plc address. But using lookatlan and scanning 192.168.200.0 to 192.168.200.255 comes up empty. I am going to try 192.168.0.0 to 192.168.255.255 next but takes awhile.
 
Yup, just start Wireshark and plug in the PanelView to your local switch.

Set the Wireshark filter to "arp" and you'll know the IP in just a few seconds. The Source field will even be labeled "Rockwell_xx:yy:zz" because PanelView terminals (like most A-B products) have a Rockwell Automation -specific organizational identifier as the first part of the MAC address.

Also, most touchscreen PanelView Standards show a white square in the lower left corner on bootup... touch it and it should go to the Configuration screen.
 
Last edited:
Try connecting to the RS232 port and upload the program. Then view the communication setup.
You will need a straight thru cable and the DF1 driver in Rslinx for this.
 
Mickey what fun it uploading the file? I usually learn a lot more doing things the hard way.

I would use AngryIP scanner and try that first.
 

Similar Topics

Hello , Does anyone know if it's possibel to comunicate a Panel View 600 to a SLC 5-05 CPU with a direct cable RJ45 POINT-POINT? ---Without a...
Replies
7
Views
1,828
I have an SLC 5/04 with 4 PanelView 600 Plus connected on DH+. Can i add a ML1400 and connect it to one of the 600's by ethernet? What I am...
Replies
4
Views
1,708
I have an older PB32 app on a PV600 that was talking DH+ to a PLC5. Well we dumped the PLC5 for a CLX and the plant exchanged the PV600 for a...
Replies
3
Views
4,053
Hey Guys. I replaced a PV600 ("old" type) today (worn out touch screen) but despite setting up the ip address and mask in the config screen, it...
Replies
5
Views
3,254
Hi All. Is it ok to use a crossover lead between a PV600 and a SLC 5/05? Info: IPA of slc is 192.168.1.2 and PV600 is 192.196.1.1 The mask is...
Replies
4
Views
1,844
Back
Top Bottom