Ic693niu004

milo_IDT

Member
Join Date
Jul 2012
Location
Santiago
Posts
23
I need configure PAC system RX3i with Expansion Modules for Local and Remote I/O (module IC693NIU004) General Electric, is that possible?.
Thanks
 
Yes, using Proficy Machine Edition, "Add Target > GEIP Remote I/O > Series 90-30 Ethernet" as a new "Target" in the RX3i Project.
 
thanks russ, I comment more about my project, I buyed a rack IC694CHS392 and a power supply IC694PWR330, according a technical specification I found. But according to what you say, this rack is not compatible with the module IC693NIU004, is that ok?.
thanks,
and sorry for my very poor english
 
The IC693NIU004 is a specialty CPU and needs a CPU chassis or rack.
Either the IC693CHS391 for 10 slots or the IC693CHS397 for 5 slots. You can still use the IC694PWR330 and most of the other IC694xxxyyy I/O modules.
 
RussB, I try of integrate this configuration, but not compatible in PME alone allow serials IC693 for modules and power supply o I have to add the generics modules
 
RussB, I try of integrate this configuration, but not compatible in PME alone allow serials IC693 for modules and power supply o I have to add the generics modules
You will be able to use IC693xxxyyy in software and IC694xxxyyy in the hardware for most modules.
 
thank for your help, at the end change the modules IC694 for IC693.

after will be open another thread, that could be help me
 