1746-HSCE (SLC) Encoder program

Is it possible to load in a new number into the encoder everytime I do a soft reset. For example firs SR load in 500 counts then the next SR load in 1000 counts etc..
 
It will be a lot more efficient to do the math at controller level.
I would write similar ladder logic for 500PPR and 1000PPR and "switch" between recipes when the soft reset is triggered.
 