Hello, we've had some troubles with measuring the resistance of thermister for a while. We use 2252 NTC Thermistors. For the PLC side, we use AB CompactLogx and the module connecting to thermisters is 1769-IF16V which read analog voltage input. From the resistance versus temperature for thermistors table, the reasonable resistance range is between 1740 to 9600 ohm. We designed the simple voltage divider circuit with 24V applied to it. Basically it's just adding a resistor in serial with a thermistor. We tried using 18K resistor. Some thermistors read a reasonable voltage, some don't (at first read fine, but later the voltage drop to about half the value as before). We suspect it may because of self heat. So we tried using resistor with higher resistance, like 50k and 100k but the problem persist. Am I missing something here? How will you connect the PLC to thermistors?

Thank you everyone!
 
Last edited:

Thanks Mickey! I checked the links. Do those transmitters output 4-20mA only? The PLC module we have now only read voltage input (0-5V, 1-5V or 0-10V)
 
One thing you did not state is the temperature range for the stated resistance range. Thermistors are very sensitive to body heat from the fingers. I am using a 500 Kohm thermistor that varies between 75F and 400F for a 480Kohm change in a voltage divider connected to a Siemens S7-200 PLC. I have no problems with the voltage divider circuit .
 
One thing you did not state is the temperature range for the stated resistance range. Thermistors are very sensitive to body heat from the fingers. I am using a 500 Kohm thermistor that varies between 75F and 400F for a 480Kohm change in a voltage divider connected to a Siemens S7-200 PLC. I have no problems with the voltage divider circuit .

Hi, thanks for the reply. These thermistors were placed down the ground for geothermal reasons. From the table, the resistance of the thermistors change from 1160 ohm to 76000 ohm. If your thermistor has 500 Kohm, then it could be quite different from ours.
 
Thanks Mickey! I checked the links. Do those transmitters output 4-20mA only? The PLC module we have now only read voltage input (0-5V, 1-5V or 0-10V)


Then put a resistor across the card's input terminals.

250 ohms give you 1-5 volts
500 ohms gives you 2-10 volts.

Then just do the engineering units scaling in the PLC.
 
Then put a resistor across the card's input terminals.

250 ohms give you 1-5 volts
500 ohms gives you 2-10 volts.

Then just do the engineering units scaling in the PLC.

Oops, how dumb I am to forget this! :eek:

I think we'll try fixing the voltage divider circuit first before buying these transmitters for economical reasons. But it's good to know that these options are available.
 

Similar Topics

Does anyone have any recommendations for Electronic Circuit Breakers with 0V Terminals built-in and Fieldbus (IO-LINK, MODBUS TCP, EtherNet/IP?)...
Replies
2
Views
186
Hello everyone, I'm having trouble selecting the right circuit breakers for the "line side" of my VFD. The common advice is to check the...
Replies
21
Views
1,344
Hi everyone: we have Baumuller AC drive BM4463 300A 160KW, it drives Baumuller AC motor DST2-315BO54W-020-5-A (90KW;RPM 200; 365V; 215A;83Hz)...
Replies
2
Views
359
Hi all, I'm working on a safety circuit and had some question about fusing. Incoming supply - 120V/15A Power supply - PSL-24-060...
Replies
5
Views
561
Been struggling to wrap my head around this all day, maybe someone else has an idea. I've got a pressure sensor connected to a 1771-IFE analog...
Replies
3
Views
621
Back
Top Bottom