Hi - I am currently working on a system and would like to use a compactlogix L35E processor in the main PLC enclosure and control Flex I/O in two or three remote RTU's. I did a system like this with SLC505, scanner module to Flex I/O over to remote I/O adapters. The processor will also be on a network with a SCADA system. Can I just connect directly through this same network to the Flex I/O and what adapter modules are necessary in the remote RTU'S? Appreciate any advice. Thanks
 
You need the Flex I/O modules to be controlled by a Compactlogix which is replacing the 5/05? Or does the 5/05 stay put and just need to share I/O infomration with a Compactlogix to be added?

You can replace the Flex adapters with 1794-AENT or 1794-AENTR modules and replace your blue hose with Cat5E and managed switches or "embedded switch technology" enabled devices.

That would be the best leap forward eliminating the SLC in my opinion. Then you can add the modules into the I/O tree of the Compactlogix.

If you are also reusing SLC 1746 series I/O, check out the "1747-AENTR". Finally, SLC i/o on Ethernet I/P!
http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/migrat-pp004_-en-e.pdf
 
Last edited:
Thanks for your reply - Yes the SLC500 is gone. Compactlogix at the main PLC enclosure and then media converters to fiber out to the RTU's, back to ethernet to Flex I/O. Can the SCADA system (just one I/O server) be on the same LAN?
 
I guess i didnt explain the SCADA part well. -- Proficy ifix running on a 2003 server box. The machine runs an OPC server (AB's IGS) and iFIX an OPC client driver to poll the field.
 
In general: Yes, you can run both I/O and ordinary SCADA communications on the same Ethernet network.

Ideally, you'll have managed switches to help monitor the utilization and quality of the important I/O cables.

With the advent of "unicast" I/O connections on EtherNet/IP, managed switches are not as important in keeping the I/O traffic away from the SCADA and enterprise traffic. They're still important for diagnostics.

Any modern (v17+) CompactLogix and 1794-AENT should support Unicast connections. They became the default method in v19, I think.
 

Similar Topics

Hi all! Having a bit of a brain cramp at the moment... I should be able to communicate to a Powerflex 700 AB drive, from a 5/05 via ethernet...
Replies
16
Views
11,121
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
257
can the slc500 5/05 send a email and text over Ethernet ?
Replies
3
Views
185
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
389
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
Replies
15
Views
2,832
Back
Top Bottom