Demonstrating a VFD

dogleg43

Member
Join Date
Dec 2005
Location
Indiana
Posts
520
We have to do a factory demo in our shop showing the usual stuff like making sure the HMI talks to the PLC, PLC controls the I/O and to a couple of 40HP ABB VFD's. The VFD's are at our shop too.

Here's my question: is it OK to just hook up a small 3ph motor to the VFD output? Obviously we don't have a 40HP motor here.

Since we'll have to buy or scrounge a motor up for this how small can we go (1/2HP, 1HP)?

NOTE: I have a call into the drive manuf's tech support to get their opinion but they haven't responded yet.
 
I don't know which model drive you are using but, in general, if you leave the drive in Scalar: V/Hz mode, you can connect a small motor (say 1/2 hp) and all will be well.
 
Almost all inverter drives will run a small motor when set to factory default settings. As long as you aren't doing anything strange with the control setup you should be fine.
 
I don't know which model drive you are using but, in general, if you leave the drive in Scalar: V/Hz mode, you can connect a small motor (say 1/2 hp) and all will be well.

It's an ABB ACS800 model.

We're not doing anything special, just 4-20mA control.

Thanks for everyone's time.
 
just try it, when the motor can have the voltage its oke.
only ramping will be different as this is current sensitive.
 
On the ACS800, it is important that you go into Parameter 9904 and set it to Scalar. Also, you must put the motor nameplate data into 9905, 9906, 9907, and 9908.

Otherwise, you will get............nothing! The 800 ships defaulted as a precision vector drive and it has to be pulled a bit out of shape to get it to act like an ordinary V/Hz drive.
 

Similar Topics

Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
119
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
152
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
85
Hello, I'm trying to delve a little into rs-485 communications for a couple projects of mine. Until now I've been using a delta vfd and a delta...
Replies
2
Views
106
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
107
Back
Top Bottom