I know a motor run status is a discrete input into a PLC but how does a motor or VFD create that input?

From the most common type of VFD's and motors

Thanks
 
Most VFDs have a relay output for run status with a SPDT (Single Pole Double Throw) contact, one normally open close on run, and one normally closed open on run. Most motor starters have an auxiliary contact on the starter coil that changes state (from open to cloed or vice versa) when the starter pulls in.

There are lots of variations on these, so I always try to get specific info on the device I'm monitoring.
 
To clarify, a motor is not normally used to create a PLC input, but the motor control devices (motor starter or contactor, and circuit breaker) is used to control auxiliary dry contacts that do provide inputs to a PLC. There are some possible motor direct inputs, such as centrifugal speed switches and temperature switches, but those would generally not be used for typical motor control logic.
 
To echo Toms reply but add a point, as far as I have seen evey VFD I ever worked on has a set of nc,common, no contacts to get run status. What I have found is they are NEVER clearly lableds as such. Not wanting to be "that" guy, looking into the user manual for your specific drive will shed light on this. TL;DR Yes they do have a status contact, good luck finding it....
 
Noob, probably the reason the relay is not clearly labeled as to function is that the function is changeable in the drive parameters. In some of the drives I am familiar with, that relay can be set up to do about 30 different things.
 

Similar Topics

I had bought a used PLC before but I had to return it. Once in a while its run mode shut off momentarily. I had the PLC on my desk. (No I/Os...
Replies
22
Views
5,375
Is there a Bit or Word that I can read remotely, from an HMI in this case, to know if the PLC is run mode, or not? Right now I just have a tag...
Replies
7
Views
1,997
Hello. I am new with PLCs, and I am working on modifying code for a non-production system with no safety implications. We are using an...
Replies
7
Views
2,313
Does anyone know if the Siemens S7-1200 family of processors has a register I can watch to see if the processor is in run mode? We have a counter...
Replies
5
Views
8,549
Hello: We have a number of Ti555's around the patch. Most are hooked up to our process network and I would like to remotly check the status of...
Replies
5
Views
2,974
Back
Top Bottom