I have 4-20mA temperature transmitter, temperature indicator (which can read 4-20mA signal), analog input card 1762-IF4 for ML1400. Here we needed to take temperature readings at two different places, thats why 4-20mA signal coming from temperature transmitter is first given to temperature indicator then its given in series to PLC.
When temperature is 25 degress actual, then temperature indicator shows correct value, but PLC shows lower value (18 degrees). Why? I checked I/O configuration where data format is "Scaled for PID". In ladder, for SCP, input min is 0 & Input max is 16383, scaled min is 0 & scaled max is 150. scaled min & max are correct as these values are set values for that temperature transmitter which also I entered in temperature indicators setting. Everything looks correct, but then why I am getting lower temperature value? Is this due to losses in transmission? Should i use proportionally lower value for Input max ? Because ideally if input card is set as scaled for PID then for 4mA it should give 0 & for 20mA it should give 16383. Here for 25 degrees it must give 4095.75 Am I correct? I checked the actual temperature with handheld laser temperature indicator it also shows 25 degrees.
Where is the problem?
When temperature is 25 degress actual, then temperature indicator shows correct value, but PLC shows lower value (18 degrees). Why? I checked I/O configuration where data format is "Scaled for PID". In ladder, for SCP, input min is 0 & Input max is 16383, scaled min is 0 & scaled max is 150. scaled min & max are correct as these values are set values for that temperature transmitter which also I entered in temperature indicators setting. Everything looks correct, but then why I am getting lower temperature value? Is this due to losses in transmission? Should i use proportionally lower value for Input max ? Because ideally if input card is set as scaled for PID then for 4mA it should give 0 & for 20mA it should give 16383. Here for 25 degrees it must give 4095.75 Am I correct? I checked the actual temperature with handheld laser temperature indicator it also shows 25 degrees.
Where is the problem?