The # indicates indirection. I will have to be careful not to explain it wrong, so I'll stop on that subject, but

Also note the size mismatch between the data types. In a COP instruction, the destination determines the size of each element, so if the destination is a Float, thats 32 bits per chunk and five chunks. This means that you are copying 160 bits (10 integers or 5 floats) from the Source to the Destination. In your case the source is a float and the destination is an INT so with a length of 5, you are copying 80 bits, or 2.5 floats!

The COP is a bit for bit image...the MOV will do data type conversion.
 
Even simpler.....

It indicates that the address you see is the starting point. #F8:61 with a length of 5 indicates that we will start copying at F8:61 and grab five consecutive values. That means F8:61, F8:62, F8:63, F8:64, F8:65 are your source data.

If your destination is #N80:43 then the destination will start with N80:43 and continue through N80:47.

So,

F8:61 is copied to N80:43
F8:62 is copied to N80:44
F8:63 is copied to N80:45
F8:64 is copied to N80:46
F8:65 is copied to N80:47

Hope that helps.

OG
 
Thanks.
So a copy instruction with the source being #I:1.0, Destination being #N23.0 with a Length of 4.
What would this mean?

Thanks
 
...
So a copy instruction with the source being #I:1.0, Destination being #N23.0 with a Length of 4.
What would this mean?

Assuming that you meant N23:0 for the destination, 4 elements (16 bit integers in this case) will be copied beginning at I:1.0. Exactly which input words get copied would depend on the I/O configuration of the PLC.

It might be:
I:1.0 -> N23:0
I:1.1 -> N23:1
I:1.2 -> N23:2
I:1.3 -> N23:3

Or:
I:1.0 -> N23:0
I:2.0 -> N23:1
I:3.0 -> N23:2
I:4.0 -> N23:3

Or something else entirely. It depends on what cards are in those slots.
 

Similar Topics

Hello everyone, Recently, my Archestra IDE shut down while I was editing. After restarting the IDE, I noticed warning symbols under my opened...
Replies
1
Views
94
I was looking for this function, so that i doesn´t need to do it in the PLC. If there are an alarm in the alarm list, i want to flash the...
Replies
2
Views
488
Hello, fairly new to plcs I’m tasked with installing a PE to a micrologix1200, in the attached picture I/14 is the PE I’m installing it’s going to...
Replies
6
Views
935
Hello Thank you all for your support. I am actually experience same issues with TIA portal V17 update5 as well as V18. The problem is with the...
Replies
0
Views
794
Hi all, I've inherited someone else's program and can't for the life of me figure out his use of the # symbol in one of his structured text...
Replies
5
Views
1,909
Back
Top Bottom