Hi,
I'm new to analog World!

I Have solar Sensor(5volt), Which output varies from 0 to 200Kohm. which I need to connect to siemens(24 Volt Modules) Analog Input (ET 200s - 2 AI I 2 wire ST, 4 - 20 mA) , HOW? what r the converters required?....PLs Help
 
If you have a 0 to 200Kohm output sensor and you want to convert to 4-20mA, you need an R/I converter from PR Electronics or other supplier.
 
http://www.electro-meters.com/Hsiang_Cheng/Transducers/SP_Series/SPR_Series.htm

Has what you want, but you will have to special order your resistance range.

The product page:

http://www.electro-meters.com/Assets/PDF_files/HsiangCheng/Transducers/SP_Series/spr.pdf


But if it were me I would go with the Red Lion converter.

http://www.clrwtr.com/PDF/Red-Lion-Controls/Red-Lion-AAMA-Signal-Conditioners.pdf

Just put your sensor in series with a 250K resistor (or a 200K resistor in series with a 50K potentiometer). Apply 10 volts across the series resistance, and pick your sensor voltage between the mid-point and ground. When the sensor "reads" 0 ohms, you will get 0 volts which the Red Lion will convert to 4 ma for you, and when your sensor reads 250K ohms, the voltage will be 5 volts which the Red Lion will convert to 20 ma for you.

I included a simple drawing for you.

CDS to 0-5 Volts.png
 

Similar Topics

I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
8
Views
125
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
141
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
75
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
54
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
Replies
1
Views
74
Back
Top Bottom