S7 200 communication problem

sweaty

Member
Join Date
Oct 2012
Location
UK
Posts
2
Hi all,
I`m having problems communicating with an S7 200 Siemens plc.
I`m using a siemens PG programmer and RS232/ppi cable. All Dip switches seem correct, i`m scanning with all baud speeds selected and i'm on the correct com port. My programmer is seeing the plc, but it is classified as "unknown" and I cannot access its program or download to it.
Does anybody know what the "unknown" label indicates?
Thanks.
 
Unknown, means it can see a device but doesn't know what it is.

A few things to try:

Do you have another PLC or cable, try using those to narrow down the problem to possibly being a bad port or cable?

Unknown can pop up if the baud rate is wrong, I think I remember a check all baud rates box that you can check.

Try cycling power on the PLC.

Try putting the PLC into "Stop" mode instead of run. It is possible to configure the ports for a "Freeport" mode, that you wouldn't be able to communicate with in run mode.
 
I have another (brand new) rs232/ppi unit which gives me the same result. I also took the programmer to another machine with an S7 200 in it and it flagged that plc up as unknown too..this is very strange as i was communicating with this device 2 weeks ago with the same set up. I have the 'all baud rates' box ticked too. Tried with the plc in 'stop' with no success. If i try to communicate with an omron plc, with its respective omron lead, it connects first time, so I know my port is correct too. Thanks for your reply Joltron.
 
its been a while since i used a S200 but this sounds like a cable problem, i know you tried a brand new lead, but i think if you go to comm devices installed ( like ppi cable, cards etc) and remove the ppi cable, then install new device for the new cable and try that, sorry i can't remember the exact path to do it but i definitely had that problem when trying to use a brand new cable
 
What kind of PLC are You using and what version of software ? Maybe updating Microwin will help ?
 

Similar Topics

problem in communication between micrologix 1200 & Panel View 600 Plus by serial DF1 Hello Friends i have to do communication between micrologix...
Replies
6
Views
6,604
Hello Friends, I'm facing a communication problem between the PC and S7-200 PLC(CPU 226) via Micro/WIN software and USB-MPI adapter, the settings...
Replies
5
Views
1,518
Hello someone please help me. I am trying to connect online on S7-200CN CPU- 226 CN. I have Micro/win software installed in my Laptop. I have MPI...
Replies
11
Views
11,368
Hi, Recently I was forced to replace a S7-200 CPU 226 on an old machine, which was defected. Unfortunatelly the old cpu was password protected by...
Replies
4
Views
1,696
Hello Guys, I'm using S7-200 PLC to run Conveyor System. I have a problem in communicating S7-200 PLC when the conveyor system starts to run. I...
Replies
3
Views
1,691
Back
Top Bottom