This one has been proven to be a real stumper, any help would be appreciated.
CPU 316-2 DP
When adding a Wincc Flex connection to the existing PLC, very odd communication stuff starts happening.
Right now the PLC is talking over ethernet to another PLC, and two WinCC stations. It also is talking to a small OP over profibus.
When I enable comm to the PLC from the new WinCC Flexible station (50 bytes or so), we start getting intermittent comm to the WinCC stations over ethernet, and the OP station over profibus. This new WinCC Flex is also talking to 5 or so other PLCs without problem.
Even more perplexing is that on two occasions, after a powercycle, the analog inputs froze. Had to turn off the WinCC flexible and cycle power to get the analogs reading again. no fault on PLC while this was happening.
I know that the PLC will give out connections as they are requested, not sure why this would affect IO (analogs on an IM365 remote rack). Anyways, this PLC should have more than enough connections.
I tried to change the connection settings to dedicate more OP connections and such, but saw no difference. Tech support didn't think that would make a difference, nor would changing the CPU comm processing from 20% (I tried 50%). I tried anyways, and they were correct, no difference.
Any ideas?
CPU 316-2 DP
When adding a Wincc Flex connection to the existing PLC, very odd communication stuff starts happening.
Right now the PLC is talking over ethernet to another PLC, and two WinCC stations. It also is talking to a small OP over profibus.
When I enable comm to the PLC from the new WinCC Flexible station (50 bytes or so), we start getting intermittent comm to the WinCC stations over ethernet, and the OP station over profibus. This new WinCC Flex is also talking to 5 or so other PLCs without problem.
Even more perplexing is that on two occasions, after a powercycle, the analog inputs froze. Had to turn off the WinCC flexible and cycle power to get the analogs reading again. no fault on PLC while this was happening.
I know that the PLC will give out connections as they are requested, not sure why this would affect IO (analogs on an IM365 remote rack). Anyways, this PLC should have more than enough connections.
I tried to change the connection settings to dedicate more OP connections and such, but saw no difference. Tech support didn't think that would make a difference, nor would changing the CPU comm processing from 20% (I tried 50%). I tried anyways, and they were correct, no difference.
Any ideas?