I am using allen bradley MCS star software to select a breaker and busbar and it is asking for max available fault current and I don't know waht that value is not the correct way to calculate it.

the service feeding this busbar will be 100 amp and come froma 100 mcc bucket.

How can I find this value or is there some value I can use that will cover all bases?
 
I am using allen bradley MCS star software to select a breaker and busbar and it is asking for max available fault current and I don't know waht that value is not the correct way to calculate it.

the service feeding this busbar will be 100 amp and come froma 100 mcc bucket.

How can I find this value or is there some value I can use that will cover all bases?

A Google Search will let you find how to Calculate the Fault Currents. Basically it is the Impedance of the Transformer, size of Feeders, and Distance.

I presume you meant 100A Bucket, does it have Fuses, or a Breaker?

Are you trying to Calculate the Fault Current at the MCC Bucket, or at the new 100A Bus?

Stu....
 
I see most breakers and such are either 50ka or 65ka. If i get everything 65ka will the system be safe without doing the calculations?

There is no way of knowing without doing the Calculation.
You need to know what the available Fault Current is, for the Circuit and location you are protecting.

Stu....
 

Similar Topics

I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
100
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
212
Square-D Symax SFI-324 I have used the SFI-510 card for many projects, but I came across a SFI-324. Does anyone have ant tech info on it?
Replies
0
Views
77
Hi, I am looking for some help with a GE Fanuc Versa Max Micro Controller model IC200UDR001-BF connected to a Quickpanel mini display...
Replies
3
Views
145
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
132
Back
Top Bottom