Hi.

This is my first post.

I am trying to configure a message block in 5000, Release 13 and I get a response that states that the instruction cannot be edited. Is this because I am using release 13?

I ask because examples I find online tell me to set the block to a specific type.
 
Bernie, I know that the MSG instruction and rung edit restriction is true of the MicroLogix 1100 and 1400 controllers.

But I don't remember that restriction on any version of ControlLogix.

Mike, are you sure the controller itself is not in hard RUN mode ? You cannot edit any rung or instruction unless the controller is in Remote Run, Remote Program, or Program modes.
 
The MSG can be edited online (even in v13), however, you must start a rung edit first, then access the MSG Configuration settings. If you access the Configuration settings without starting a rung edit then you cannot accept the changes.

OG
 

Similar Topics

Hi Is it possible to use message blocks in Step 7 similar to RSLogix. In RSlogix I can use message blocks to read/write info between 2 plc's...
Replies
2
Views
1,787
hi everyone, i have problem regarding Audit in FTV ver 12,In audit message "service disruption:<HMI server name>:<SERVICE NAME>" message logged,i...
Replies
1
Views
37
Is there a way to add a local message display to Studio 5000 View Designer? If its there, I’m not finding it. I have used them in older versions...
Replies
11
Views
406
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
131
I have a safety PLC AB that is stuck trying to charge the capacitor and will not do anything. No communication or anything can be done. Is there...
Replies
0
Views
67
Back
Top Bottom