Controllogix and Prosoft Profibus MVI56

pauly

Member
Join Date
May 2002
Location
South Wales,U.k
Posts
244
We have a MVI56-PDPMVI profibus master card in a Controllogix rack communicating to a single slave. Every 10 -20 minutes or so the MVI56 card goes into stop, the COM STAT LED goes off and the MSTR STAT LED goes red. This conditions remains for a second or less and the card comes back to life and communication is restored. We have changed the MVI card for a new one out of the box but we still have exactly the same problem. Is there any setting in either Prosoft control builder or the RSLogix 5000 software that might cause this problem? Any advice is appreciated.
 
We have a MVI56-PDPMVI profibus master card in a Controllogix rack communicating to a single slave. Every 10 -20 minutes or so the MVI56 card goes into stop, the COM STAT LED goes off and the MSTR STAT LED goes red. This conditions remains for a second or less and the card comes back to life and communication is restored. We have changed the MVI card for a new one out of the box but we still have exactly the same problem. Is there any setting in either Prosoft control builder or the RSLogix 5000 software that might cause this problem? Any advice is appreciated.

Terminator turned ON at both ends of Profibus connectors?
 
I am new to Profibus also, but in my system I do a sync as follows, do not know if it help with your issue, you may try it out

Sync CRC.JPG
 

Similar Topics

Hi guys, Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap: 1. Existing Profibus...
Replies
5
Views
3,227
I've worked on a handful of projects that relied on a Prosoft module for Modbus comms with other systems (older PLCs, boilers, chillers, much...
Replies
5
Views
2,144
I am not very experienced in Rockwell PLCs and have run into a small problem, so I could do with a little bit of help. We have a redundant...
Replies
3
Views
2,496
Good Evening , I'm looking for ways to log tags from a ControlLogix PLC. Have any of you used ProSoft PLX51-DL-232 Data Logger ? It...
Replies
0
Views
1,098
1) I am currently trying to integrate a Prosoft MVI56E-MCM Module into a 1756-L61 CONTROLLOGIX5561 that is a redundant system (CPU is redundant...
Replies
13
Views
3,408
Back
Top Bottom