Factory Talk ME Alarms

suraj2k

Member
Join Date
Nov 2012
Location
Calgary
Posts
12
Hello,
I am trying to setup alarms to display on an alarm banner on a specific display 'Display1'.
I dont have a physical HMI, so i'm testing my displays by hitting the 'Play/Test Display' button.
Problem: In 'Test Display' mode, when an alarm condition occurs, the alarm banner remains blank.
Setup Method:
Triggers tab: I've setup one alarm (alarm1) as a trigger, trigger type = value, trigger label = alarm1. (alarm1 is a boolean PLC tag)
Messages tab: Trigger = {[PLC]alarm1}, Trigger Value = 1, Message = 'common alarm', Display = checked, Print = checked
Advanced tab: Display Current alarms: 'Display1'. Everything else is default.

What am I missing? What kind of setup do I need on the alarm banner itself, that sits in 'Display1'?
Thanks
 
When you use the "Test Display" function, FactoryTalk View just runs that one Display.

It doesn't run the Alarm subsystem, the Macro subsystem, the Global Connections susbsystem... just the one Display.

If you need to test the Alarming system, use the "running man" icon to start a Test Runtime. You'll see all the FactoryTalk services start running (in the FT diagnostics banner) and the whole project and all of its features will run.
 

Similar Topics

Hi all, I am currently having an issue with 3 HMI panel view panels with the alarm list showing the incorrect date and time. It shows up as the...
Replies
2
Views
2,238
Hi All, I am trying to make the machine to stop with an alarm “clean lid welder required “ every 10000 cycles. I can trigger an alarm in logic...
Replies
2
Views
1,355
Good day I want to know if it is possible to set up the historical alarms on a Allen Bradley HMI without using a SQL server ? Is this possible...
Replies
1
Views
1,457
So I have Factory Talk ME ver 12 and Studio 5000 ver 32. Hardware is a 2711P_T7C21D8S 7" Panelview Std connected to a CompactLogix L30ER. I am...
Replies
6
Views
2,273
I'm a bit lost when it comes to alarming in Factory Talk SE. ALMA/ALMD device based alarming is pretty straight forward: all state is is in the...
Replies
2
Views
5,550
Back
Top Bottom