Hi: I have an SLC5/03 faulting (major fault) from time to time due to "50" errors " (A chassis data error is detected on various slots). My question is...is there any way to stop the major fault from happening for these faults, until we can get a look at the noise and possible chassis issues, as recommended by Rockwell? This is a very non-critical application and lost or corrupt chassis data for even a few seconds would not cause anything dangerous or destructive. Has anyone seen a method to prevent hardware errors from shutting down the PLC? ;)
 
There isn't.

If the error was limited to a specific slot and that slot wasn't critical, you could inhibit the slot and the controller would ignore errors from that module.

But SLC-500 controllers are fanatically protective of their I/O integrity, and check the backplane for errors every scan. In the SLC operating system, if anything's "out of control" then it shuts everything down.
 
Hi Ken: That doesn't surprise me because of potential "abuse". What do you recommend for intermittent "A50, B50, and C50" errors? Where do you start when it comes to possible noise causing this. Noise where? On the PLC power supply input, or?? Slot A is a RIO scanner, B and C are analog input cards. Only see the fault on these slots. Thanks!!
 
If you're getting faults on all three slots, there's likely a grounding problem.

Start by double-checking the bonding of the SLC chassis (there should be a threaded post on the bottom of the chassis) as well as the ground terminal on the power supply.

Next, lift the shield wires on each analog input and on the RIO cable, and check for any voltage to ground.

Damaged or defective SLC-500 chassis and power supplies are notoriously difficult to detect except by replacement. The SLC is so popular and so reliable that these are uncommon, but by no means unheard of.
 
Hi Ken: That doesn't surprise me because of potential "abuse". What do you recommend for intermittent "A50, B50, and C50" errors? Where do you start when it comes to possible noise causing this. Noise where? On the PLC power supply input, or?? Slot A is a RIO scanner, B and C are analog input cards. Only see the fault on these slots. Thanks!!

I'd probably get a look at the noise on the RIO scanner and its cabling and/or inhibit the slot fault as noted above. :whistle:
 
One other thing to look at...I have seen faults like you are describing on a couple different machines we have here. These machine vibrate and shake pretty violently and regularly and the problem ended up being a bad chassis.

Hope this helps
-Dave
 

Similar Topics

I have a packing machine that is running a SLC5/04 for the past 20 or so yrs, that we are upgrading to a spare 5/05. After changing the...
Replies
3
Views
1,360
Hello All, When trying to go to RUN mode the processor faults and I get this error. Error description is: Remote Power Failure of an expansion...
Replies
5
Views
2,785
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,551
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,269
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
634
Back
Top Bottom