Siemens Failsafe Signal Modules

PeterW

Member
Join Date
Jun 2006
Location
Calgary, AB
Posts
2,531
For the first time I'm working with the failsafe safety modules and one little thing is annoying me in that there appears to be no information.

When you assign the addresses to the cards, there is always an output area associated with the input cards and vice versa for the output cards.

When you click in hardware profile to edit the symbols, only the inputs turn up.

I cannot see where you would use the outputs, reading the manuals they only mention the outputs in the tech specs stating how much of an allocation.

Anyone know;

Why they allocate outputs?

and How and why do you use them?
 
Peter

Im sure I have some detailed info
but the short of it is that it is your F safety process image

You will need to monitor the "pass_out", "qbad" etc
 
The Safety integrated system uses the extra I/O address space for the send/receive of a CRC based telegram. Each end monitors the telegram and if a problem is encountered, the plc can report it and the safety outputs can go to their fail safe state.
 
Thanks, mystery solved.

Wish they state that in plain site, had me wondering if there was supposed to be something important I should be doing with it.
 

Similar Topics

I have a Siemens S7-414 PLC that has, among other things, one ET200SP rack that has one safety F-I/O card (6ES7136-6BA00-0CA0) (two emergency...
Replies
2
Views
1,556
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
28
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
94
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
281
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
97
Back
Top Bottom