analog resolution with omron

rock

Member
Join Date
Aug 2003
Posts
35
what is the max amount of resoulution possible with omron plc?

need 16 bit, but best I can tell, 12 bits is the max.

Need to try and figure out how to connect a wheat stone bridge type load cell to a plc module.

thanks
 
I used CPM1-MAD-11 analoge input which give 1/6000 resolution.
Its not 12 bit (4096) and not 16 bit but it work good with weightig
head analoge output.
 
The CPM1 MAD01 is 1 to 255
CPM1 MAD11 1 to 6000
C200H ad003 1 to 4000
CS1W AD081v1 1 to 4000 OR 1 to 8000
CJ1W AD081V1 1 to 4000 OR 1 to 8000.

For devicenet look at the DRT1-AD04H devicenet analogue cards, they can give you 1 to 32000.

Here's a thought about a weigh cell...

You say that you want 16bit ( lets assume 1 to 32000) and you are measuring a silo (that just so happens to be mounted outside).
And...lets assume that 1kg = 1 bit.
If you are using a single point detection won't the enviromental conditions such as wind or temperature affect the readings. It won't take much.. I believe that you could use two weigh cells and average the difference to give a more accurate reading.

Well thats my 2 cents anyways....
 
Whill I reading Sleepy post I rememberd that I made something like that with RS232 I added 2 ports to my CQM and connected to the scale
You can do it also with RS485.
Just a thought.
 
CS1W-PTS11 is 16-bit and accepts +/- 100mv.
CS1W-PDC11 is 16 bit and accepts 4-20ma, 0 to 5vdc, +/- 5vdc, +/= 10vdc, 0-1.25 vdc, +/- 1.25vdc.
All of the above are isolated inputs.
 

Similar Topics

Hi, i am new in this field i want to know what is mean by analog card resolution pls help me
Replies
1
Views
2,332
i've dealt mostly with the PLC5 in the past, but i'm getting ready to do some work with a SLC. what is the input resolution of the i/o...
Replies
1
Views
3,134
N
I am little embarassed to ask this question but I thought this would be the place since the people here are so receptive to people new to the...
Replies
7
Views
9,282
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
111
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
112
Back
Top Bottom