I am trying to integrate Power Logic PM750MG with my RTU. My RTU cannot read the C phase-neutral or C-A phase to phase voltage. If I use modscan program I can read all the values without any issues. Can anyone assist me. Thank you.
 
Can your RTU read any value or values correctly from the Power Logic?

If so, is the format different for those values it can read versus those the RTU can't read correctly?
 
Hi I can read all other phases. Having issues with C phase and C-A. Same for both integer and floating value. For example when the PT value is full scale for all three phase. Modbus value for Phase A and B is full scale, 0 for C phase. Phase to Phase value is full scale for AB and BC, half for CA. LCD display full scale for all phase.
 
>Phase to Phase value is full scale for AB and BC, half for CA. LCD display full scale for all phase.

Apparently you can read values from the Power Logic into the RTU, but you do not believe the values are correct. Hence it is not a comm hardware layer issue.

Whose LCD display? The drive or the RTU? Is this the source of the discrepancy?

>If I use modscan program I can read all the values without any issues.

If Modscan can read the correct values (how do you know they're correct values?) from any or all registers in the Power Logic, then as a Modbus slave, the Power Logic is not the problem. The hardware transfers the contents of the registers.

Some issue in the RTU . . . . display not reading the register that you think it's reading???
 

Similar Topics

Hi everyone, I'm trying to simulate any program in control expert and see a register in Modscan32 or any software to do that (Like ModbusPoll). I...
Replies
0
Views
91
I have a Type C to RS485 adapter connect to my Siemens RWF55. I use modscan to scan it to get a value from the Siemens controller. In the...
Replies
4
Views
93
Dear All, I could not get the results with modscan software to test the Modbus connection for the digital relays. The modscan software says...
Replies
3
Views
4,900
Good Day, I'm using Mod Scan 232 for testing a Modbus RTU network on RS 485. The modbus device is Accuload iii.net. The connection settings on...
Replies
1
Views
4,159
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
6
Views
55
Back
Top Bottom