Hi friends
I am doing a Project with S7-200 Plc. All are digital input and dihital outputs only.
But my project spec reads a line as follows:
" The PLC system should be communicated with the DCS system thru RS485 communication"
I havent done this before. Please help me for the instruction.My CPU model is CPU-226.
Do we nee to use modbus lib instruction for this?
Thanks
 
MPI and Profibus are also RS485.
To specify a connection to a DCS as just "RS485" is not detailed enough.
It is most important that the protocol is exactly specified. Dont just assume a certain protocol, get it confirmed.
 
Hi
The protocol is MODBUS.
The PLC is programmed to be the MODBUS Slave.
The Slave is the Client's DCS. The DCS is supposed to be in the site in Qatar.But we need to test or scan the outputs thru the MODBUS in the Factory during FAT.HOw do we do it?
We tried to use MODSCAN in our PC nd connect to the PLC , But we are unable to connect. Is there anyother way to check the outputs thru the MODBUS?
chitra
 

Similar Topics

Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
252
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
127
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
Replies
1
Views
179
Hi Experts, I would like to make firmware upgrade from v3.0 to v4.5 (S7-1200 CPU 1215C). Can I do it from v3.0 to v4.5? Do I need to take some...
Replies
6
Views
285
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,856
Back
Top Bottom