about 1756-IF16 module

angi

Member
Join Date
Jan 2010
Location
us
Posts
361
hi guys

I am confused about how to use 1756-IF16 in Single ended mode, please see my attachend picture, in the picture, is the "user provide loop power" a power supply of transmitter or a power supply for the module? why there is no power suply for the input0?

thanks
 
The diagram you have posted shows the two possible alternatives.

The upper part of the picture shows a device connected to IN-0 via the two-core shielded, twisted pair cable, and that device is capable of driving the 4-20mA signal current that the IF16 needs. By inference, then, this device (which isn't shown on the diagram), is powered from another source, most likely it is powered from 120Vac or 24Vdc. This is known as an Active device.

The lower part of the picture shows a device that receives its power from the 4-20mA loop that the PLC input is monitoring. Such a device is classed as a Passive device, or "loop-powered". Obviously a loop-powered device itself must not consume more power that would exceed the 4mA minimum signal current. So assume the device itself requires 2mA to power the device's electronics, then it will regulate additional current through itself to "signal" 4mA to 20mA for the working range of the device.

In either case, the transmitter device needs power. Active devices just drive the 4-20mA signal through the analog input module with a current generator, while Passive devices "steal" their power supply from the loop, adding additional current to provide the required 4-20mA signal.

In the diagram, the "User-Provided Loop Power" must be a "stable" power supply, (usually 24Vdc), which must be provided for Passive 4-20mA devices.

It is generally not recommended to use the same power supply that powers 24Vdc Inputs and Outputs, although many people do this. It all depends on the capability of the power supply to maintain a constant voltage with a variable load, and the quality of the loop-powered devices to reject or filter out line supply noise.

So typically a control system will have separate 24V power supply modules, one for powering digital inputs and outputs, which needn't be that good at line/load regulation. And a second for powering "loop-powered" analog transmitters, which would be a much smaller supply with good line/load regulation specs. This, IMHO, is "best-practice".
 
Last edited:
thanks Daba

is Active Device a 4 wire transmitter?

In the diagram, the "User-Provided Loop Power" must be a "stable" power supply, (usually 24Vdc),----- how to provide a Loop Power if the transmitter requires a AC power, for example, 120VAC?
 
"4-wire transmitter" is often used to signify that the device needs "4-wires" - two to power the unit, and two for the 4-20mA signal that goes into the PLC.

If you have a device that requires external power, then it is an "Active" device, and you must provide the required power supply for the device.

"Loop-Powered", or "2-wire" devices do not need a power supply, they take their power from the measuring circuit.
 
Hi Daba

could I connect a 4 wire transmitter using Single Ended mode?
if I want to configure a Singlr Ended current mode, no matter the transmitter powered by same power supply or not( either 24VDC or 120VAC), I just make sure to use the same Loop power(the same 24VDCC), is it correct?

thanks
 

Similar Topics

Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
131
Is there a way to see what the actual field signal value is going into each channel of the Analog Input I/O card 1756-IF16? In other words, I...
Replies
4
Views
3,650
I have a 1756-IF16 Analog Input Module. It is setup for Differential Mode. I am trying to read the 4ma to 20ma signal from a flow meter. I am...
Replies
49
Views
11,850
Hi, Last week I faced a problem with a 1756-IF16 analog input module. All the channels being used started showing 15-20% greater values than...
Replies
3
Views
4,512
I have a 1756-IF16 module wired for single-ended inputs,that has 2 channels (6 & 14) which will go to zero randomly.I have swapped out the module...
Replies
1
Views
3,215
Back
Top Bottom