AB Micorlogix 1000 panelview hookup

gafry

Member
Join Date
Oct 2002
Location
Denver,Pa.
Posts
14
I have a micrologix 1000 that I would like to connect with a

panelview for graphics. What do I need for this connect as far

as cables and software. thank you
 
Please provide the complete catalog number of your PLC and your Panelview.

And what software/cables you already have.
 
The 2711-B6C1 terminal is intended for use with larger PLC systems like the PLC-5, and is equipped with a network port for the PLC-5's remote I/O protocol, called Allen-Bradley Universal Remote I/O, and nicknamed "RIO".

There is no way to connect that protocol to a MicroLogix 1000 controller.

Although the PanelView does have an RS-232 serial port, that port is used only for upload/download of the application program and cannot be used for runtime communication with a controller.
 
A Panelview component is pretty inexpensive and does not require you to buy software to program it. In fact, buying one of these is probably cheaper than Panelbuilder32 (for old Panelviews) or FactoryTalk View Studio (for Panelview Plus) software. Only issue real issue with Panelview Component is they do not work with Logix5000 controllers.
 
The 2711-B6C1 terminal is intended for use with larger PLC systems like the PLC-5, and is equipped with a network port for the PLC-5's remote I/O protocol, called Allen-Bradley Universal Remote I/O, and nicknamed "RIO".

There is no way to connect that protocol to a MicroLogix 1000 controller.

Although the PanelView does have an RS-232 serial port, that port is used only for upload/download of the application program and cannot be used for runtime communication with a controller.


What would be a good HMI panel interface for the Micrologix 1000
I want to set up some graphics for the program
 

Similar Topics

We install a lot of stand by generators at residential sites. I have started using micrologix 1000 controlers for load shed of the air...
Replies
8
Views
3,028
This may be a stupid question, but I have several Compactlogix controllers that are using consumed / produced tags to transfer data between them...
Replies
12
Views
3,271
Hello all I am looking for some assistance in connecting a Micrologix 1200 (1762-L40AWA) to a SLC5/05 (1747-L551C) via a 1761-NET-AIC module. The...
Replies
0
Views
2,069
after going online with a micrologix 1200 It will no longer communicate with the panelview plus 700. I powered it down went online and backed up...
Replies
2
Views
3,230
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
126
Back
Top Bottom