PID S7-1200 can't enable.

phongnhatdo

Member
Join Date
Mar 2012
Location
Singapore
Posts
38
Dear all.
my problem is PID can't enable after run PLC and active rung, you can see image below.
PID1_zps1fd76229.png

I was tuned in windown commissioning and up load parameter to project. when satus controller is enable-automatic/manual, this time PID active. But after I stop PLC or power off and restart PLC then PID inactive.o_O
I'm using TIA v11.0
hepl me. I want to PID compact alway active...
 
Thank JRW so much.
I was clicked on link system block/ program resource/ PID_Compact
it display " the current block is write protect because it is know how protect" and tilte " PID_compact controller with self-tuning"
I'm offline with PLC.
The first time download to PLC then PID remains mode " inactive". next step is open commissioning windown for tuning? it is require of program? can bypass step tuning because system on mode manual parameter pid?
hope that get share from everybody.
Thanks.
 
a ơi có phải muốn nó auto thì set 3 vào chân Manual value của nó ạ ?

Thank JRW so much.
I was clicked on link system block/ program resource/ PID_Compact
it display " the current block is write protect because it is know how protect" and tilte " PID_compact controller with self-tuning"
I'm offline with PLC.
The first time download to PLC then PID remains mode " inactive". next step is open commissioning windown for tuning? it is require of program? can bypass step tuning because system on mode manual parameter pid?
hope that get share from everybody.
Thanks.
a ơi có phải muốn nó auto thì set 3 vào chân Manual value của nó ạ ?
 

Similar Topics

Hello all, I have set up a PID loop which works fine except it is a bit slow during the startup. I wish that it would reach near the setpoint...
Replies
1
Views
1,832
how can i use pid+pwm to control brightness of the ac light
Replies
4
Views
2,241
Hello everyone, this is my tutorial for using PID function on S7-1200. Hope you guy like it. https://www.youtube.com/watch?v=INB6_7SqeOg
Replies
0
Views
1,636
Hello everyone, I'm new in using plc software. I want to set a parameter for my centrifugal pump using an i/p from PID block so that the range of...
Replies
0
Views
1,282
Hello, I changed controller type in RSLogix 500 from SLC 5/02 to MicroLogix 1200 and was given the ladder logic to update it for the new...
Replies
25
Views
4,822
Back
Top Bottom