We are having a new line installed and we have specified to a supplier that all 42 PF40's have their own 22-COMM-E adaptor, ontop of that their will be 12 1734-AENTR's and 1 PV+1500, and we want to then have it connected on the Plant Control Network to interface with other controllers, and monitor the drives and also some Server based SCADA package which has yet to be confirmed, we will then want to do product tracking all the way through the line, they are wanting to use a L3, 1769-L33ER processor now i have reservation that this will be lacking in processing power/connection to do all that we want.
they have also ignored our requests and quoted for 11 ethernet cards to sit on 22-XCOMM-DC-BASE and use RS485 for Run source and speed, the plan is to have 11 remote panels around the line, and in each panel an unmanaged weidmuller switch (IE-SW-BL08-8TX), 1 1734-AENTR and 1 22-COMM-E and between 3-4 PF40's in each, then each box back to the main panel with another unmanaged switch in it.
i have suggested we upgrade to ControlLogix and i emailed the supplier the list below:
I propose a 17 slot ControlLogix rack configured as such:
1756-A17 - RACK
1756-PA75 - PSU
SLOT 0: 1756-L71
SLOT 1: spare
SLOT2: spare
SLOT3: 1756-EN2T (I/O)
SLOT4: 1756-EN2T (DRIVES)
SLOT5: 1756-IF16
SLOT6: 1756-IB32
SLOT7: 1756-IB32
SLOT8: 1756-IB32
SLOT9: 1756-IB32
SLOT10: spare
SLOT11: spare
SLOT12: 1756-OB16
SLOT13: 1756-OB16
SLOT14: 1756-OB16
SLOT15: 1756-OB16
SLOT16: 1756-OB16
And in replacement of the 3 off 1769-IT6 cards a 1734-AENT with the appropriate amount of 1734-IT2I modules which would be located externally from the main panel to suit your system.
the supplier has quoted an extra 17,000 Euro's for this upgrade even though the cost of the upgrade in terms of components is around 7-8k, i could just use 1756-ENBT modules but even with that saving it will take some persuation.
i could do with some advice on if this is overkill going to ControlLogix or if its warranted, and if so some supporting arguments, as the guy in charge of the project is relluctant to spend anymore money on this £12 Million project.
Thanks in advance
Rob
they have also ignored our requests and quoted for 11 ethernet cards to sit on 22-XCOMM-DC-BASE and use RS485 for Run source and speed, the plan is to have 11 remote panels around the line, and in each panel an unmanaged weidmuller switch (IE-SW-BL08-8TX), 1 1734-AENTR and 1 22-COMM-E and between 3-4 PF40's in each, then each box back to the main panel with another unmanaged switch in it.
i have suggested we upgrade to ControlLogix and i emailed the supplier the list below:
I propose a 17 slot ControlLogix rack configured as such:
1756-A17 - RACK
1756-PA75 - PSU
SLOT 0: 1756-L71
SLOT 1: spare
SLOT2: spare
SLOT3: 1756-EN2T (I/O)
SLOT4: 1756-EN2T (DRIVES)
SLOT5: 1756-IF16
SLOT6: 1756-IB32
SLOT7: 1756-IB32
SLOT8: 1756-IB32
SLOT9: 1756-IB32
SLOT10: spare
SLOT11: spare
SLOT12: 1756-OB16
SLOT13: 1756-OB16
SLOT14: 1756-OB16
SLOT15: 1756-OB16
SLOT16: 1756-OB16
And in replacement of the 3 off 1769-IT6 cards a 1734-AENT with the appropriate amount of 1734-IT2I modules which would be located externally from the main panel to suit your system.
the supplier has quoted an extra 17,000 Euro's for this upgrade even though the cost of the upgrade in terms of components is around 7-8k, i could just use 1756-ENBT modules but even with that saving it will take some persuation.
i could do with some advice on if this is overkill going to ControlLogix or if its warranted, and if so some supporting arguments, as the guy in charge of the project is relluctant to spend anymore money on this £12 Million project.
Thanks in advance