I've got an ungrounded 600VAC system of motors that is only operated periodically, and it has some offline ground fault detection. However this only is functional when the control power for the system is active, and therefor not always available, since this system is only activated periodically. The HMI's associated with the monitoring system are only powered on when the system is activated, which is usually a few days before use so that it can be checked out.

I are debating whether we should re-design so that the ground fault system is always on and has some kind of permanent notification, or whether its simple enough for the operators to just flip it on a few days before use and then find out if a ground fault had developed. I'm concerned that if we go to a lot of trouble to make the ground fault detection system always operational, that nobody will really pay attention to that system until they are ready to use it anyway, which is what happens right now (considering that this system is isolated from other systems)

Has anyone dealt with a situation similar to this or have any opinions or considerations?

Thanks!

$
 
I would opt for permanent monitoring. In order to get them to pay attention set up timers that will force a shut down when timed out. It works for use here... 4 hours to fix the problem or else.
 
One installation I worked with had used 3 CT's (VT's? my electrical hat is sitting crookity) to light bulbs, say 480v-120v. When the bulb was out, you had a loss of phase. Really low tech. It's easy to connect the 120V, or whatever voltage you need to a PLC for monitoring.
 
The problem here is the contactors.
When using offline, you should close all contactors without having the main breaker on.
Now you can see a fault in any motor.
it means all contactors must be on, and this means you will have to redesign your system to have a separate power system for the control.
example when you switch on a light the fault can be on, but away when switched off.
when i am doing groundfault tests every piece of equipment must be switched on. especially the firepump (i work a lot on commercial ships.)
 
You make no mention of what ambient conditions exist around this equipment. I think that is most important to know. Humidity temperature variation, dust, etc etc. You also make no mention of equipment size or value.

From shipboard experience our two main problem sources were water oriented - either condensation or saltwater intrusion into equipment - especially DC.

I think at the minimum I would do meggar check on motors a week before startup. That may allow enough time to dry out a motor or do other repair work.

I do not see the justification for ground detector when equipment is deenergized. Meggar will work just fine.

Dan Bentler
 
You make no mention of what ambient conditions exist around this equipment. I think that is most important to know. Humidity temperature variation, dust, etc etc. You also make no mention of equipment size or value.

From shipboard experience our two main problem sources were water oriented - either condensation or saltwater intrusion into equipment - especially DC.

I think at the minimum I would do meggar check on motors a week before startup. That may allow enough time to dry out a motor or do other repair work.

I do not see the justification for ground detector when equipment is deenergized. Meggar will work just fine.

Dan Bentler

I had all this typed out then read what Dan said ... I concur...:

If you have a megger, you should do a megohm test of all the motor circuits before you close the main circuit after being offline. I would think you will find your ground faults quickly that way and be able to isolate them to a particular motor circuit in most cases.

If you have contactors that all drop out, you can do a quick meg test of the motors from the bottom (disconnected output side) of the contactors. This will prove the whole motor circuit except for the contactor itself. If you expect or wish to test the contactor too, then yes you need remote power and a separate isolator (probably interlocked) and would have to disconnect wires from any VFDs or softstarters before you run the insulation test..

I don't like to touch any local motor disconnects during the test as opening and closing them (in the wet food environment especially) can mask symptoms or temporarily hide a fault. If I find a fault, then I look to split it among the cables and devices downstream but always try to test the whole circuit from the last protection device onward at first. During PM most of the time, it will test good, and you move on to the next motor.
 
Last edited:

Similar Topics

We have a 753, 75 HP, driving a centrifugal pump, that has been giving us ground faults for months. The drive has load, and line reactors. We have...
Replies
19
Views
8,453
Hey all. I dont know if this belongs here but I have a High Resistance Ground unit that is displaying a resistor fault. Anyone have knowledge on...
Replies
8
Views
2,842
Hello guys, I am facing the ground fault problem often. We have a liquid mixer machine and the motor is installed under the mixer tank.so...