I have cpu313c but in cpu I have no conter,DI8*DC24V,AI5/AO2*12bit,DI16/DO16*DC24V with firmware v2.0.8.By the way I also have done hardware update but no result.
 
The provided CPU nr does have an onboard counter. 3 actually.
In the HardwareConfig it is part of the CPU.
2. CPU
2.2 Digital IO
2.3 Analog IO
2.4 Counter

Double click on Counter to configure it.
 
The image of the terminals in the 313C CPU is wrong.
There are 40 terminals also in the left-most terminal block.

Also, both terminal blocks images are wrong. The terminals are not marked 0-7, 0-7, 0-7, 0-7, but 1-40.
 