Hi,

I have a couple of Unidrive SP VSDs running in Open loop mode that have developed faults over the last month. The drive setting "3.48 - Position Feedback intialised" somehow gets turned on and is not editable. Even a factory reset does not reset the position feedback setting.

It has resulted in one VSD ramping up and down uncontrollably given a fixed speed reference, and one trying to run at 0.8Hz both with a minimum speed clamp of 20Hz.

Has anyone else had issues with these drives?
 
UniDrive SP

Good Evening,
Do you have a encoder connected to the drive or an option module. Its my under standing that if an encoder is detected parameter 3.48 will be set to 1.

Try disconnecting or encoder to see if 3.48 sets back to 1 after a factory reset.
Also I dont think it is necessary to save the changes when doing a factory reset but give a try.

Have A Good Day
Tom
 
There is no encoder attached to the drive, only a Profibus DP module.

I tried removing the Profibus card and carrying out a factory reset but the setting still turns on again as soon as the reset is complete.
 

Similar Topics

Looking for a Modbus address manual for M700. Modbus address is same as the Parameter number for 16Int parameters. But it is different for 32Int...
Replies
2
Views
1,985
We have an EN214 base drive fitted with an FM3 module that has started to drop out of its program at random and then start again after a few...
Replies
0
Views
1,155
I have a Emerson Motion Controller Control Techniques Ei202 servo drive Indexing With motor NTE-207-CONS Brushless servo motor Issue 1 Every...
Replies
0
Views
1,430
Has anyone used a Control Techniques M701 Drive? I am wondering about using the built in PLC?
Replies
3
Views
1,592
Can anyone show any worse example for this indescribably tacky marketing approach for industrial components? Control Techniques make GREAT drives...
Replies
1
Views
3,762
Back
Top Bottom