Schneider PLC

mariobo11

Member
Join Date
Sep 2012
Location
Universe
Posts
62
Hy,

I have new problem...:(

73159864.png


What means that sign at my PLC card? It is not accepting my analog 4...20mA signal...

Anyone?

Thank you!

Kind regards,

Mario
 
Last edited:
Yes...It is OK configured and it cant be that kind of error.

If there is that kind of error, can other modules communicate with PLC? (Two from the right).

o_O

One another hint... I have tried to remove third module and i did another hardware configuration, but again, third module was in fault just like that one before. Modules were different.

Anyone?
 
is there power present at module? I have see'ed same mark at online only if module is different or missing (broken?)

How about the module numb two. Have you tryed change it to new one?
Bus goes trought the modules so try changing also module two.You can also swap modules one and two. If fault goes to different module (= module2 is then faulty one)
 

Similar Topics

Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
103
Hi Please I have zeilo smart relay #SR2A201BD but I don't have it's programming cable. Can I use any general usb/rs232 converter? Or need...
Replies
3
Views
158
Trying to identify the Modbus RTU registers that are in use in the Function block programming in the PLC program. I have a Kohler DEC 550...
Replies
0
Views
155
Hey all, I do not have the original source code of a Modicon M172 PLC (HVAC PLC). I want to modify some of the code but read you cant upload...
Replies
2
Views
339
Hi All, We are planning Establish communication between Power Energy Meter (Schneider PM5320) with Rockwell PLC. I am unable to get the Assembly...
Replies
4
Views
755
Back
Top Bottom