Hi,
I have a PLC S7-1200 with CPU 1214C and a CB 1241, RS485 module.
and i want to read holding registers from a Schneider protection relay S42 and T40 like volt and current, from the Schneider protection relay data sheet S42 the data addresses and encoding with a factor of 10 (x10) the start address is 0136 until address 0150 (total of 27 addresses), i think this means the start address DATA_ADDR is 40311 with length DATA_LEN is 27 but i don't the other values of the MB_COMM_LOAD and MB_MASTER, do you have any ready program?

Thanks in advance
 
I would use a Modbus test program on the PC (modscan) first to check out the adressing. It is easier to do changes and see the results.

You will need an converter to RS485. Search eventually for 'poor mans RS485'.

Kalle
 

Similar Topics

Hi All, I am trying to communicate siemens PLC with FESTO Servo & 3 Festo make Steppers on FHPP Modbus Protocol. Sometimes, I face Modbus...
Replies
0
Views
1,326
Should it be possible to upload hardware and software with TIA from a controller that has 3rd party profinet I/O (Muir) Impact67? I have only...
Replies
1
Views
1,103
Hello all; I need to create a software program that is a stand-in for a PLC I/O card. My program will be controlling a coordinate measuring...
Replies
11
Views
3,358
Hi All, I am looking to see if anyone has had this issue before. I have a TIA portal on site which is programmed in TIA Portal V13.0 but the...
Replies
3
Views
3,525
I am unable to get a frimware update for the above mentioned hardware. After days of waiting and few emails back and forth to...
Replies
8
Views
4,613
Back
Top Bottom