panelview plus question

stu

Member
Join Date
Aug 2005
Location
England
Posts
783
Hi I have a question,
I have a project that I would like to put a password on I have set up a user eng and entered a password ,put a login button on the screen changed display which I would like password protected , but when I test application and logged in it said I died have access and ideas thanks
 
After you create a User, you go into the Runtime Security configuration in FactoryTalk View Studio and select which security level (A, B, C, etc) each User has.

Security generally applies to a Goto Display button. Is that what you created and tested ?

The FactoryTalk Diagnostics log is very helpful in diagnosing permissions and user login history.
 
Hi Stu,
From memory you just go to "users and groups" and expand the dropdown. Here you see "user". Highlight this right click and choose "Add New". Choose the new user name and password and Don't Forget to Click box "Password never Expires". Click OK and Exit.

Then go to system and expand the dropdown, click Runtime security. Choose show all users and choose your new user "Eng" and set the access levels that you require for each display by clicking the boxes. Close and save and you should be done.

From what you describe you have carried out this process but did you remember to click password never expires checkbox?

Regards,
Donnacha
 
You "tested" the application? I'd create the runtime, transfer it and run it to test it.

If it does look like you aren't logged in, you might look at your Project Settings and see if the "Enable auto logout" is checked and if so, what the Inactivity Period setting is. You may be getting logged out, almost as soon as you log in?
 
Hi guys I have another problem I have adjusted the PvP screen and made sure the runtime ect is setup when I try to create a runtime it comes up with " unable to save rslinx enterprise data server info ? Any ideas
 
Last edited:
Got the software working , after hours of fun I deleted rslinx enterprise for the second time and re installed all working again thanks for your help guys
 

Similar Topics

Hi guys I have a question about panelview plus hmi I understand that there are 2 types of factorytalk software SE &a ME Which do different things...
Replies
2
Views
1,477
Hello, I am able to use the ME transfer utility (and see the panelviews in Rslinx) when I connect to an Panelview Plus Compact 600 271PC-T6C20D...
Replies
2
Views
3,278
Long story short, I have several of these panelview plus 1000. they are interchangeable, so the programming is all the same. every so often when...
Replies
2
Views
2,488
Hello, I currently have a Panelview plus that is communicating with a PLC 5 on DH+. I plan on moving this panelview to another location on the...
Replies
3
Views
1,751
In my project, I have a Panel View Plus 6 1500 communicating with a ControlLogix L61. My issue is I have about 80 screens and when the user...
Replies
22
Views
8,703
Back
Top Bottom