I am trying to program a controllogix with a 1756-dnb card to operate a powerflex 700 drive with a 20-comm-d card in ladder logic programming. Any help will be appreciated.
The actual Address will depend on your I/O Mapping in the Logix DNB. It doesn't necessarily go with the Node Address, so you will have to get that from your RSNetworx for Devicenet. I usually setup an Excel Spreadsheet to keep track of everything when I do a Devicenet System.
I try to use a common setup and then use COP to map them into a couple of UDT's
(one from, the other to the drive) so I do not have to remember which bit (or INT) does what
- The UDT also helps in self documenting the code. (or use the Devicenet tag generator - never had much success with that)
Ask yourself will you ever need datalinks? it's always easier to add now than later
If the link is not used much then allow in the DNB mapping so addresses do not change later.
what I need is a step by step tutorial on setting this up and programming it. does anyone know where i can find one? I've tried to decypher the original program for info but it's so proprietary, I can't make heads or tails of it.
what I need is a step by step tutorial on setting this up and programming it. does anyone know where i can find one? I've tried to decypher the original program for info but it's so proprietary, I can't make heads or tails of it.
The Program doesn't know, the Programmer does. The only thing that matters is where the Programmer mapped the I/O in the DNB Scanner with RSNetworx for Devicenet.
I've got RSNetworx for DeviceNet but the existing program was configured with RSLinx.
Not possible. RSLinx is required to access the network, but RSNetworx for Devicenet in some form or fashion is required to configure the scanner. I think some version of RSLogix5k may inegrate RSNetworx for Devicenet but still there is s scan-list. Look for that *.dnt file Stu mentioned. If you don't find it, you can upload it from a running scanner.