Panelview 600 and Controlnet

Bolatov

Member
Join Date
Jun 2010
Location
Mty
Posts
87
Hello

I need to do some modifications to a PV600 standard terminal that uses Controlnet communications. I dont understand how does the Tag addressing is mapped, those numbers in red SI0:1 alike cant be find in the plc program or tags instead they kind of look like this PV_N03:I.Data[15]

but how can i know how are these mapping related?

i was checking the AB literature but didnt find something really useful.

Thanks a lot

dudas.JPG
 
The RSNetworks file you have posted is "Read Only"; in order to access the Scanlist Configuration mapping you will need to access the Keeper's Scanlist; if you have the RSNetworx for ControlNet software, open-up the file, highlight the 1788 bridge (Keeper) and then, within the Menu bar, choose the Device tab and then pick Scanlist Configuration; the PV to FlexLogix mapping will be listed within.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/cnet-um001_-en-p.pdf Chapter 7
 
Last edited:
Panelview Controlnet Tag Addressing Solved

Wow!!

Thanks a lot for the fast response Mickey and dmargineau, that pdf was the literature i was looking for.

The RSNetworx didnt let me use the scanlist configuration, maybe its because the 1788 is old or maybe my RSNetworx version is old.

But anyway thanks a lot guys you're great!!!

Made tests and everything is working fine!!!
 
Almost done

Thanks for your help so far it has been great!... im amost done... but if i put the tags anywhere in the program they show the mistake 9128

It says something like "Tag cant be readed from the controlnet scheduled file"

What could be happening?

controlnetfail.JPG controlnetfail2.JPG
 
Last edited:
FAilure

New, i could put pushbuttons into the Screens but when i put it on the alarms it says the same mistake 9128
 

Similar Topics

I tranfer the .mer file to the panelview plus. So when I run application, it's seem application doesn't work. The data just display ***** and...
Replies
2
Views
2,148
I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
Replies
12
Views
220
Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
455
Hello, Friends Please someone help me find right cable to communicate Panelview 600 (2711-B6C9) to Micrologix 1200 (1762-L24AWAR). AND any advice.
Replies
3
Views
269
Hello , I have an HMI of PV+ 600 (2711-T6M5D) Ser A Rev B, This HMI doesn't have the ethernet port i have to take backup through communicate...
Replies
5
Views
650
Back
Top Bottom