flex I/O 1794-IE8

Sammy Murai

Member
Join Date
Feb 2013
Location
Rua Marechal Dutra 414 - Campinas
Posts
1
Hi, i have a configuration whit 1747-SN and 2 racks in flex i/o (1794-ASB).
In the rack 1 i have 4 modules 1794-ie8, 3 modules 1794-oe4 and 1 module 1794-ia16. In the rack 2 i have 5 modules 1794-ia16 and 3 modules 1794-oa16.
All digital modules are ok, i see the sinal in the PLC. But the analogical modules don't have any sinal.
Somebody have any idea???
Tanks

Samara Cibele
 
Last edited:
Analog module data does not show up in the input and output data tables like the digital modules. You must program a BTW and BTR for each analog module. In those BTW and BTR instructions, you will need to specify integer data table addresses for the data that is written to the module and for the data read from the module. The Input Values for each input module channel will then show up in the integer data table.

To make it easier, make sure that your IO Configuration is setup to show the proper cards in the proper location. If you do that, the BTW and BTR instructions will have a "setup" that you can click to get some guided help in seting things up.

Don't know that I'm explaining that clearly - doing it from memory. Go to the AB website and download the literature for your analog modules. I believe you will see expamples for what you need to do.
 

Similar Topics

Can anyone give me an idea of what the I.Fault and I.Status represent on a 1794-IE8? I can't locate this info in any documentation.
Replies
3
Views
4,304
Hi, I am back again, still with the issue of getting the 1794-IE8 configured and getting the reading from 1794-IE8. I am using SLC 5/04 series C...
Replies
1
Views
2,341
Hi guys, Recently one of our AB Flex 1794-ie8 Series A analog input module has failed and we replaced it with a new one but a new module is Series...
Replies
8
Views
10,672
New at this so here it goes, Could anybody give me a basic overview of what this type of FLEX I/O does, its an '8 input analog module...
Replies
2
Views
4,836
D
Have a small problem, when setting up 1794-IE8 using 4-20mA signal. With RS 5000 is there a way to offset the counts 0-33840? Im not sure how the...
Replies
0
Views
4,410
dougiediner
D
Back
Top Bottom