I was told by the user manual and by users that if you have a solid red fault light then the CPU is shot and it needs to be repaired

I bought a L35e and was flashing it up to V19, a few minutes into the flash it faulted, see below for the code from the flash.

Code:
03/01/13 10:02:27 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server. 

03/01/13 10:02:39 [SUCCESS] Load Driver: C:\Program Files\Common Files\Rockwell\AB_ASA.DLL

03/01/13 10:02:39 [SUCCESS] Initialize Driver: C:\Program Files\Common Files\Rockwell\AB_ASA.DLL

03/01/13 10:02:48 [SUCCESS] Device Identity: Path = RSLinx API!AB_ETHIP-1 16 12 49 57 50 46 49 54 56 46 48 46 52 52 1 0, Instance = 1,
VID=0x0001, PT=0x000E, PC=0x0041, Maj Rev=15, Min Rev=04, SN=0x003FD517

03/01/13 10:02:48 [FAILURE] Device Identity: Error #10003: GetAttributesAll to Device object - target returned fault status.
  Status: 0x3550

03/01/13 10:03:00 [SUCCESS] Validate: 
VID=0x0001, PT=0x000E, PC=0x0041, Maj Rev=15, Min Rev=04

03/01/13 10:03:00 [SUCCESS] Authorization: Bypass cookie used.
Key: PN-86085

03/01/13 10:03:02 [SUCCESS] Load Script: C:\Program Files\ControlFLASH\0001\000E\0041\PN-86085.nvs

03/01/13 10:03:02 [SUCCESS] Program: Catalog Number = 1769-L35E/A R15.31, Serial Number = 003FD517, Num Updates = 3, Size = 5962544 byte(s).

03/01/13 10:03:04 [SUCCESS] Update: Instance = 3, Size = 2554872 byte(s), Chunk Size = 128 byte(s), Major Rev = 15, Minor Rev = 4

03/01/13 10:03:56 [FAILURE] Transfer: Error #11006: Service cannot be performed while object is in current state.
  GS=0x0C, ES=0x3002

03/01/13 10:05:54 [FAILURE] Transfer: File = C:\Program Files\ControlFLASH\0001\000E\0041\PN-86072.bin, Block = 5724.

So I restarted the CPU and got the solid red fault, so I removed the battery and shorted the positive to the negative for a few minutes (this takes about 10 min) tried short time but it did not help

This is the 3rd solid red light that it has cleared, I don't think it will work for all solid red faults I think the solid red comes from not doing a full boot cycle so I am sure there are several reasons this may happen, I think this one was just at a bad spot in the boot cycle and could not start from the beginning until the capacitors were drained and then it would start over, the other two I received they were red (not flashing) from the start so not sure what happened to them when they faulted in the first place,they were also L32e's.

Just thought I would pass on the info and may save some people a few bucks or some time, I don't think Rockwell recommends this as a practice but if you have a faulted/failed CPU you need to try something and this may work

The second flash to this CPU went great! :)
 

Similar Topics

I have an Schneider M1E 171CBU98090 Processor adapter with only a solid red 'ERR' light lit. Manual explains flashing red ERR but not Solid with...
Replies
1
Views
1,015
Hello, I have a processor module that has a solid Red OK light. Status stuck on WAIT. I have tried the steps to clear memory/restore to...
Replies
3
Views
1,486
Hello I am new to PLCS.net, I have a question here in regards to the Network Status light being solid red on the 1734-AENT. I checked the manual...
Replies
2
Views
1,730
I bought a used L55M23 processor on Ebay and turns out that it doesn't work. RSLinx can't find it whether by RS232 or Ethernet adapter. With this...
Replies
4
Views
3,463
Kindly, we have the following module with its Module Status led solid red. What can we do to solve this? " POINT I/O EtherNet/IP Adapter Module ...
Replies
6
Views
3,914
Back
Top Bottom