Micrologix 1400 with Modbus 485 comm cable.

tactical

Member
Join Date
Nov 2012
Location
NE
Posts
41
Having trouble wiring my device into the 1763-NC01 adapter and can't find any good documentation online. The adapter has connections labeled TERM,A,B,COM,SHLD AND CGND. The device I am wiring has the following wiring guide.
2qx16w2.png

Which wires are wired where? I would assume A and B are for the +data(yellow) and -data(green) wires and the COM is for the Power 0V(Blue) wire? Thanks in advanced.
 
Last edited:
That's the way I would do it, too.

Swapping the Data A and B wires is a standard ritual of RS-485 hookup... no two manufacturers seem to designate them in the same way.

The connection of the SHLD or CGND wires depends on your cable architecture, and the connection of the TERM jumper depends on how many devices are in the system, the cable length, and the presence or absence of a termination resistor at the other end of the cable.
 
That's the way I would do it, too.

Swapping the Data A and B wires is a standard ritual of RS-485 hookup... no two manufacturers seem to designate them in the same way.

The connection of the SHLD or CGND wires depends on your cable architecture, and the connection of the TERM jumper depends on how many devices are in the system, the cable length, and the presence or absence of a termination resistor at the other end of the cable.

Okay thank you for your response. Now if I want to power the device. Do I plug the Power +12V (red wire) into the +DC OUT on the MS 1400 and then take a wire from the -DC OUT and connect it to the COM port on the Modbus 485 adapter?
 
In general, it is best to keep power and communications connections separate.

This device seems to use the "Power 0V" terminal as both the communications and the power common terminal, so you're forced to have both communications and power referenced to the same common terminal.

If you do use the sensor power supply on the MicroLogix 1400, use the +DC and -DC terminals together.

I don't know for sure if the Channel 0 RS-485 COM terminal and the -DC terminal on the MicroLogix 1400 sensor power supply are internally connected or not, but they're definitely not intended to be used interchangeably.

Usually I recommend against using the sensor power supply for anything but sensors: it is very small (I think 250 mA) and shorting or overloading it tends to cause the MicroLogix to fault.
 
In general, it is best to keep power and communications connections separate.

This device seems to use the "Power 0V" terminal as both the communications and the power common terminal, so you're forced to have both communications and power referenced to the same common terminal.

If you do use the sensor power supply on the MicroLogix 1400, use the +DC and -DC terminals together.

I don't know for sure if the Channel 0 RS-485 COM terminal and the -DC terminal on the MicroLogix 1400 sensor power supply are internally connected or not, but they're definitely not intended to be used interchangeably.

Usually I recommend against using the sensor power supply for anything but sensors: it is very small (I think 250 mA) and shorting or overloading it tends to cause the MicroLogix to fault.

The unit I am hooking up requires 80 mA at 12 Volts.
 
I made this document a while ago. I don't bother buying the 1763-NC01, I just mash a standard MiniDIN-8 cable into the port. They go in nicely and stay tight since the guides on the cable housing dig into the molded plastic of the socket. I get the MiniDIN-8 cables as straight through male-male cables from L-COM and cut them in half. I reference the L-COM color codes on this document.
 

Similar Topics

I want to learn about modbus communication and I saw on another thread about inexpensive modbus relay units so I found it on Amazon along with a...
Replies
46
Views
7,206
I have a spare Micrologix 1400 Series B I bought used on Ebay awhile back. I had thought of it as a spare PLC for my train project but I screwed...
Replies
4
Views
1,243
Good Day! Would anyone be able to explain what is happening with the COP's and MOV's in this Modbus poll routine? If anything I am confused by...
Replies
6
Views
1,728
I been tasked with setting up communication between a heating cooling unit manufactured by Advantage Engineering and a Microloagix 1400 plc. The...
Replies
6
Views
2,499
Hi, I am trying to communicate between a MicroLogix 1400 and a Click PLC. There is a great video from AD that shows the simplicity of...
Replies
2
Views
1,762
Back
Top Bottom