hello,
device can be read via Modbus ION7550 with a GE RX3i PLC, do not allow me to place a read address above 32767, as I can do to extend that value

:sick::sick::sick::sick::sick::sick::sick::sick::sick::sick::sick:
 
hello,
device can be read via Modbus ION7550 with a GE RX3i PLC, do not allow me to place a read address above 32767, as I can do to extend that value

:sick::sick::sick::sick::sick::sick::sick::sick::sick::sick::sick:
Proficy ME lets me use any valid value I want for the assigned "Data Type". Exactly where are you attempting to use this "Unsigned Integer" value within PME?
Is it in Logic, a Parameter for a Function, Configuration of a module?
Here is a screen shot that may help: ( For reference only, the value 33721 really should be 0 here.)
I am using Proficy ME 7.50 SIM3 here.

UINT_1.jpg
 
Last edited:
hello,
That is, I need to put the address I have to point in that direction and ION7550 is 40150, then to set the value and throws an error compiling, but apparently achieved by placing the block UINT do.
Now try, then you commented, thanks
 

Similar Topics

I want to realize the communication S7 and pc by cable profibus or mpi I want to know the steps to that allows me to do it
Replies
0
Views
1,263
good day everyone. right now i troubleshoot a STACKER MACHINE. the fault in the PLC CPU315-2 pn/dp is BF1 and SM fault. I check all the...
Replies
4
Views
2,064
Hello , I have the classical configuration of CPU315-2DP + 5 * ET200 , just long time did not work on this configuration , the switch of Profibus...
Replies
11
Views
2,623
Dear Sirs, I had a problem with CP 343-1 with CPU315-2DP.I had newly add the CP343-1 Ethernet module to the hardware to allow me to access this...
Replies
5
Views
2,624
Hello Can any body help me for communicating Deltav and PLC(Cpu 315-2DP)without cp342. How am I doing this configuration in PLC. Please help me.:hmmm:
Replies
0
Views
1,058
Back
Top Bottom