In the literature for the card. It says scaling for the enginieering parameters can be done in the card. It shows what the raw data for 4 and 20ma will appear as. I'm going to us 0-100 lpm flow meters on those inputs. Can I really go into the configuration for the card and put 0 for the 4ma and 100 for the 20ma and do my scaling that simply. This is kind of what the literature implies, nowhere does it just come out and say it.
 
Yep, it is that simple.
There is a caveat though: scaling directly within the module and setting the Low Engineering to 0 LPM for a "transmitted" current value of 4mA will not accomodate provisions for "electrically open circuit" conditions sensing (the sensor "outputs" 0 mA); the CPU will not be able to "detect" the "zero current" value since the proposed calibration "ignores" anything less than 4mA and accordingly placing "0" within the hardware defined tag.
 
Thanks for your help. I'm glad it is that easy. I'm adding these flowmeters, but I'm not an indepth programmer. This will really make my task easier. I understand what you are saying about open circuit detection. I'll have to keep that in mind
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
2
Views
39
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
Replies
5
Views
212
Hi all. I'm working on a rehab and I'm trying to figure stuff out. See screenshot at the bottom. Local:5:I.Data[6] in BTD instruction is a...
Replies
6
Views
701
Hello all, First post here. Hitting a wall with finding info on this topic online, and none of my coworkers have a clue. I have a PanelView...
Replies
10
Views
1,335
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
Replies
0
Views
624
Back
Top Bottom