I want to import a FB from a previous project that was in the Libset V4.0 library in unity pro xl.

I can do and export import of the project and open it in v7 no problem, also all custom FB's i created show up int he types library manager under application.
My query is it possible to import a old Libset v4.0 FB into the Libset v7.0 so I can use the FB in different programs without having to develop it every time?

Cheers
 
yes, it is possible. On Unity V4 project you can export your custom FB's to ztx format. Then on Unity V7 import these back and copy to library.

Or another way is to copy all custom FB's from library to project which is on v4 format and save project.
(open some old project first, which is on Unity v4-format, if you don't have *.sta file rename your *.stu file to *.sta and you can open it with newer Unity. on File-open window, Select libset: Keep project version )

Then on Unity open this project with file-open command and select now (libset: update with latest version available). After this your custom FB's s and project are V7 version and you can copy FB's to library.
 
Last edited:
Cheers for that. I had actually already performed this import successfully. I was a non custom block that just isn't available to the M340.

After reading further I found that the M340 doesn't support the read_reg FB which I previously used with my quantum for TCP/IP comms. I can't seem to find a way of reading data via TCP/IP modbus other than I/O scanner. See I need 2 NOR cards for DNP3 so I have to use the onboard ethernet port for TCP/IP modbus comms to my network.
 
Last edited:
Cheers for that. I had actually already performed this import successfully. I was a non custom block that just isn't available to the M340.

After reading further I found that the M340 doesn't support the read_reg FB which I previously used with my quantum for TCP/IP comms. I can't seem to find a way of reading data via TCP/IP modbus other than I/O scanner. See I need 2 NOR cards for DNP3 so I have to use the onboard ethernet port for TCP/IP modbus comms to my network.

Do you know if theres any pre defined block that can be used for TCP/IP mosbus reads?
 
I haven't used M340 PLC with Unity, but io-scanner or read_var and write_var with addm-function maybe

IO-scanner is easiest to configurate
 
Yes well I have been analyzing those options.

I just need to get my head around the GEST ARRAY input on the read_var FB ill need to do some testing here.

Have you used these functions for the other PLC's int the range.

I have digitals is another PLC that are not bit packed and I can't make modifications to that plc. As far as I can see the I/O scanner can only be used for registers and i'm also limited as the proceessors ethernet port doesn't support I/O scanning:(

Thanks for all the help mate your a gent.
 
Cheers Geoff, I have started looking at it and just need to sequence my reads / writes as I have 6 slaves.

Thanks guys
 
Guy's bit packing and unpacking in unity. What are the function blocks. I have this comms up an running but i'm looking for a way to force particular bits in the management array.
 
Bits within words and integers may be directly accessed, for example tag.0

Just make sure in the project settings - variables - Allow bit extraction of Int word and byte is ticked

There are also the functions Bit_to_byte, byte_to_bit, word_to_bit, and bit_to_word to set or examine all the bits in a word or byte
 

Similar Topics

Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
8
Views
75
Hello all, I am wanting to update the system clock via NTP in the M580/M340. I'm aware that we are able to connect to a NTP in the controller...
Replies
4
Views
115
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
Replies
8
Views
315
I'm using M340 (Schneider Electric) as modbus master. It works fine but if there is a disconnection with the slave, it stops working even after...
Replies
2
Views
421
Hello, I am trying to send sms messages using SR2MOD03 with an M340 and can't find anything related to it on the internet, can you please help...
Replies
0
Views
204
Back
Top Bottom