Wagoi 750-841 and Citect

wago841

Member
Join Date
Mar 2013
Location
InAHouse
Posts
2
hey all I'm having some problems communicating to a Wago 750-841 with citect v6.10.

has anyone here successfully got a connection between the two and if so could you share your settings or even better share a blank project with them already configured.

Thanks in advance. If you need anymore information please let me know.
 
Hi WAGO841,

Connecting to the WAGO using MBTCP is really pretty straight forward. The only "Gotcha" that I'm familiar with is the address of the first register in WAGO memory. The 750-88x controllers reserve the 1st 3000 hex registers (12288 decimal). That means that %MW0 will have a Modbus address of 412289. Please check the 750-841 manual to see how many registers the 750-841 reserves.

Good Luck

(8{)} :) .)
(Yosi)
 
hey thanks for the reply i believe the 841 is the same in regards to addresses being out by 1.

Ive taken a screenshot of my current settings which i got from using the express setup but still no luck. is there anything there that looks out of the ordinary?


2qi5ono.jpg


Thanks Wago841
 

Similar Topics

Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
78
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
120
Hello, I m having a problem with wago 750-862 plc. The plc won't start automatically in run mode after a power reboot. I've also tried the...
Replies
4
Views
347
Hello everyone, I am trying to setup a Wago 750-8100 PLC to send a text message out via ethernet port, if I get a Digital input that is true. I...
Replies
0
Views
342
Looking over the technical data for a PowerFlex 755 & noticed they specify a minimum enclosure volume for their drives: (1)When using a circuit...
Replies
1
Views
546
Back
Top Bottom