I believe we are getting somewhere now.
The news are bad though; as I have stated previously,
you will not be able to Upload a DeviceNet network scanner/devices configuration/parameters using your current resources.
You will need the RSNetWorx for Device Net (9357-DNETL3) software and a DeviceNet network-to-PC interface ( 1770-KFD, 1784-PCD or 1784-U2DN ).
Now back to the Slot 22 1747-SDN.
There are quite a few reasons you cannot choose Slot 20 (22 Logical) for the SDNPT driver deployment.
One of them, which I think it might apply here, is the 1747-SDN
minimum required
firmware revision that supports the SDNPT driver communications; this would be
4.015; if the 1747-SDN scanner carries a firmware revision
between 4.015 and 5.001(including), the SLC M files size has to be increased from default 256 words to
361 words (via RSLogix 500 Offline File + CPU Download); in order to be able to run a SDNPT driver within 1747-SDN FRN between 4.015 and 5.001, after the above conditions have been satisfied, you will also have to switch the CPU run mode from Run/Remote Run to Program Mode and then back to Run/Remote Run Mode.
Only 1747-SDN scanners carrying firmware revisions higher than 5.001 could be accessed via the SDNPT driver and I think this is your Slot 13 (12 Logical)condition.
As you could probably see, this task is quite "labor intensive" and will require several system shut-off actions; moreover, you will not be able to accomplish the task at hand (uploading the network's configuration and devices' settings for backup purposes).
Ask for (or acquire)the "colorful" resources I have previously listed;
you need them!