how to communicate Siemens s7 200 plc with honey well dc1040 temperature pid controller ?
what are the procedure we can do?
how to configure dc1040 ?
 
The DC1000 series manual from Honeywell's web site (Documents tab)
https://www.honeywellprocess.com/en...and-programmers/programmers/Pages/dc1000.aspx
says only that the communications hardware layer is RS-232 or RS-485.

It specifically states that the baud rate setting is not to be changed from the default 2400.

There is a unit ID number for the RS-485 version, but there is not a word about which protocol the unit talks.

If this unit hasn't been commissioned yet, and you have to talk to it, changing it to some other model/brand might be a prudent choice, given the lack of communications information on this unit.
 

Similar Topics

Hello Everyone, I am using Mitsubishi L-series CPU. I have a sensor that needs to be calibrated on Ethernet TCP/IP communication. Can you please...
Replies
8
Views
2,062
i have a S7 300 PLC, it was talking to an anybus X-way modbus TCP gateway vi CP 343-1, after gateway failure i've changed the gateway and load the...
Replies
1
Views
1,810
hi everybody,, Hi am using third party AB panelViewPluscompact 1000 HMI want to communicate with Mitsubishi Qseries PLC.. i update the...
Replies
1
Views
1,941
Hi, Back after a long time. And in need of help. Customer had a system where 4 equipments were being controlled by a single PCL 5/40. Each...
Replies
0
Views
3,051
Hi, I am having problem with communication via third-party Scada (Citect 7.10) to a 1761-Net-ENI, connected to a ML1200. The Scada...
Replies
27
Views
27,038
Back
Top Bottom