siggibald Member S Join Date Oct 2012 Location iceland Posts 60 Apr 15, 2013 #1 i have a pt100 4-20ma is the analog input on micrologix 1100 only for 0-10V ??
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Apr 15, 2013 #2 is the analog input on micrologix 1100 only for 0-10V ?? Click to expand... The embedded analog input is, with a 10bit resolution ( 0-1023 counts) Just put a resistor across the input terminals 250 ohms gives you 1 to 5 volts, 500 ohms gives you 2 to 10 volts. You can add an analog input module also. To accept the 4 to 20ma and give you better resolution.
is the analog input on micrologix 1100 only for 0-10V ?? Click to expand... The embedded analog input is, with a 10bit resolution ( 0-1023 counts) Just put a resistor across the input terminals 250 ohms gives you 1 to 5 volts, 500 ohms gives you 2 to 10 volts. You can add an analog input module also. To accept the 4 to 20ma and give you better resolution.
siggibald Member OP S Join Date Oct 2012 Location iceland Posts 60 Apr 15, 2013 #3 yes i know it is possible in analog input module, I'm just so surprised that it is not possible on 1100. thanks
yes i know it is possible in analog input module, I'm just so surprised that it is not possible on 1100. thanks
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Apr 15, 2013 #4 siggibald said: yes i know it is possible in analog input module, I'm just so surprised that it is not possible on 1100. thanks Click to expand... It is possible.
siggibald said: yes i know it is possible in analog input module, I'm just so surprised that it is not possible on 1100. thanks Click to expand... It is possible.
siggibald Member OP S Join Date Oct 2012 Location iceland Posts 60 Apr 15, 2013 #5 yes. I have to buy a resistor to morow