I Have a LBL instruction then later on in the ladder I have a JMP instruction back to it am I right in thinking that when the JMP instruction is true the scan jumps back to the LBL instruction thus increasing the scan time ????

Jezz

:(
 
be carefull.....

if you jump backwards too long, without hitting the end
statment, the scan watchdog will expire,
and the processor will fault.
 