I am currently looking for a solution to provide proving status of a DC motor. The DC motor I have draws maybe .4 to .5 DC amps. very small. I need to validate that the motor is on before I continue with the rest of my program. My problem is I haven't been able to find any DC current switches that can switch that low. The lowest I have found so far will make at 2.0 amps. I realize i can do multiple wraps on the CT switch but this can be unreliable at best depending on the fluctiation of the current draw. anybody have any ideas on another reliable way i can accomplish this with out using an inline relay or something? thanks for any help.
 
Have a look at the following product from schneider electric, works between 3ma and 1 amp.

RM4JA31
 
Absolute Process Instruments

You can not "do multiple wraps on your CT"

DC Current is not measurable via electromagnetic flux. (Unless using actively simulated Hall effect transducer)

I would suggest a DC Current trip relay:
APD 1000
APD 1020

These can have up o 900mA input, and digital output for your plc.

OR, if you have spare analog input, you could read the motor current direct into the PLC real time using

APD 4380
These can have up o 900mA input, and 0-10v or 4-20mA output for your plc.

http://api-usa.com/signalconditioners_dc_input.php
 
You could wrap one of your motor wires around a glass reed switch. These are magnetic, and will switch with a small dc-induced magnetic field. Cheap and simple.

Having said that - are you trying to prove that the motor is rotating? Just because it is drawing current, it does not mean that the motor is actually running.

Is there anywhere you could put a proximity sensor on a moving part to check that actual motion is happening?
 
Thanks guys...all of these are good inputs. the first item i am trying to prove i found another way however there are two actuators of which i am reversing the polarity on to open/close. I will need to validate these as well. i believe some of your replies may work for my program.
 

Similar Topics

Off topic, but you people here usually have pretty good suggestions. Title kind of says it, anyone know of a DC current switch that has a decent...
Replies
1
Views
737
Does anyone have a reputable manufacturer they use for their current switches w/ analog input?
Replies
2
Views
2,197
Today I was working on my project for school and we were using a power supply with 24V and we accidentally had the current at 0.9A. We heard a pop...
Replies
9
Views
545
Hi all, I have been working on a project that requires me to measure the current across a 90 VDC motor of a medical device (similar to an...
Replies
26
Views
1,526
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
661
Back
Top Bottom