Omron hmmmm

arkyny

Member
Join Date
Nov 2011
Location
Victor, NY
Posts
131
Anybody have experience with the Omron CJ1M-CPU2 PLC? I received a machine last week with this processor/PLC and at present acquiring the programming software. While I have run the machine without any (brain) diagnostics at the present, I am finding that it is unpredictable,eg, LVDT readings. Using Solartron LVDT sensors, on a known surface, I get different results almost after every run. The signal runs through an analog input module, then display to HMI. The device that it measures is smooth and controlled by a stepper motor that takes a snapshot every half resolution x 3. ?🔨
 
It is probably a CJ1M-CPU12.
You will require a special cable whether it be for the peripheral port of a serial port.
I would not expect the PLC analogue input to play up - more likely the device, incorrect wiring, noise.
If there are several loop powered devices wired into the same analogue input card signal isolators are required.
If the analogue input is 1-5V, 0-10V or -10/+10V I would suggest you may have to have a look and see if there is any induction into the wiring - 4-20ma is much more immune to noise.
 
You will need CX Programmer and a CS1W-CN226 cable to talk to a CJ1M PLC. There is no CJ1M-CPU2 so its either a CPU12 or a CPU21, 22, or 23.
Don't jump to the conclusion that there is anything wrong with the PLC or programming, although that is certainly a possibility. Your repeatability problem could be a poorly designed machine, or your parts could be a whole lot worse than you think they are.
I have seen more than one case where the surface finish on a part was outside the part tolerance range making it impossible to get repeatable readings.
 

Similar Topics

Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
Replies
2
Views
48
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
48
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
3
Views
88
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
251
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
4
Views
131
Back
Top Bottom