IM360 not accepted in slot 3 ??? (SIemens)

A poor screenshot, near impossible to see anything. (as usual as I am tempted to say).

It seems you have chosen an IM361R and not an IM360S.
The IM that goes into slots 3-6 in the CPU rack must be an IM360S.
(I might be wrong. Not sure based on the screenshot).
 
Hey

Hey Jesper,

I tried them all.
The message is:
Input Adress 2000 of the module (Rack 0, Slot 3) is invalid.

regards,
G

A poor screenshot, near impossible to see anything. (as usual as I am tempted to say).

It seems you have chosen an IM361R and not an IM360S.
The IM that goes into slots 3-6 in the CPU rack must be an IM360S.
(I might be wrong. Not sure based on the screenshot).
 
I could not import the entire station, since I don't have the Lenze GSD you are using.
The CPU rack imported OK though.
I could insert an IM360S in slot 3 with no problem.

Zip and post the GSD file(s) that you use in this project.
And/or try to setup a new project from scratch with a fresh new hardware configuration.
 

Similar Topics

Have a strange fault issue. New system ran for 3 days then cpu faulted out with vague error messages. Rack make up is. 315-2DP IM360 343-1 341...
Replies
9
Views
4,799
Hello, I want to find some documentation/standard on accepted percentage of no responses/timeouts. i.e. is 1/100 1/1,000 1/10,000 1/100,000. I had...
Replies
3
Views
2,600
Out of curiosity and necessity, I would like to hear from you all around the world, telling me which plc brand is prevalent in your country. This...
Replies
22
Views
6,072
Hey, I'm having a strange error on a PLC 5/40B Series D Rev B. I am trying to set the channel 0 configuration from "system (Point-to-Point)" to...
Replies
5
Views
3,431
Hey Guys, I am getting random rack/slot errors. I go to download and everything is ok but then it has a error. For example - Yesterday everything...
Replies
1
Views
363
Back
Top Bottom